消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

【常见问题】吸水管与母管、吸水管与水泵进水口未采用管顶平接

发布于:2024-11-08 14:38

【问题描述】吸水管与母管、吸水管与水泵进水口未采用管顶平接

 

《 消防给水及消火栓系统技术规范》 GB50974-2014

5.1.13 离心式消防水泵吸水管、出水管和阀门等,应符合下列规定:

    2 消防水泵吸水管布置应避免形成气囊;

 

12.3.2 消防水泵的安装应符合下列要求:

    7 吸水管水平管段上不应有气囊和漏气现象。变径连接时,应采用偏心异径管件并应采用管顶平接

 

来源:青岛市建设工程消防验收给排水专业常见问题(2024版)


请写下您的评论评论
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


评论 | 1

张治福 2024-11-11 08:18 00 [回复]举报

在需要变径连接时,偏心异径管顶平接

推荐问答

关闭

关闭

手机APP下载