消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

独立建造的柴油发电机房,是不是就没有防火要求?

阿宸宸宸宸OK | 2024-11-07 11:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

潘天坤 2024-11-07 13:29 10 [回复]举报

请问独立建造的设备用房是否与与民用建筑或者人员密集的场所贴邻?

房间隔墙根据不同耐火等级一般有0.25小时至0.75小时耐火极限要求

同时柴油发电机房等独立建造的设备用房与民用建筑贴邻时,有防火分隔要求(应采用防火墙分隔,且不应贴邻建筑中人员密集的场所)

发电机房、储油间的顶棚、墙面和地面内部装修材料有燃烧性能A级要求



阿宸宸宸宸OK   回复: 潘天坤2024-11-10 11:16

不与其他场所贴邻。独立建造的柴油发电机房耐火等级不低于二级,疏散门采用乙级防火门   这样做可以吗?

0    0 [回复]举报

关闭

关闭

手机APP下载