请问,防火卷帘门的导轨要不要做防火处理,依据哪一条规范?

忙里偷闲 | 2025-03-18 08:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

wetom 2025-03-18 14:04 00 [回复]举报

我了解的情况,供你参考。不是导轨要做防火处理,而是双轨的导轨间要防火封堵,一是满足防烟性能,二是保证导轨在火灾时不易变形。依据就是防火卷帘安装图集12J609中,双轨卷帘装饰节点的图示,双轨间全部采用防火材料封堵。

EHS专家-DL 2025-03-18 14:50 00 [回复]举报

‌防火卷帘门导轨必须进行防火处理‌,原因如下: ‌

导轨作为防火卷帘整体耐火结构的一部分‌:防火卷帘的耐火完整性要求涵盖导轨、帘板等所有组件,需确保火势蔓延时导轨不失效或变形‌。‌

防烟性能要求‌:导轨需与帘板配合形成密闭防烟屏障,若导轨未做防火处理,高温下可能变形导致密封失效‌。


规范依据 ‌

1、《建筑防火通用规范》GB 55037-2022‌: 第6.4.8条明确防火卷帘的耐火性能不得低于所在防火分隔部位的耐火要求,且关闭后需具备烟密闭功能‌。导轨作为防火卷帘的支撑和密封部件,需通过防火处理满足上述性能要求。‌

2、《防火卷帘、防火门、防火窗施工及验收规范》GB 50877-2014‌: 第5.2.2条条文说明要求导轨材质及安装应保证帘板运行顺畅。第5.2.2条中第5进一步规定导轨滑动面应光滑、平直,安装后相对于基础面的垂直度误差≤1.5mm/m,间接表明导轨需具备耐火稳定性‌。‌

3、GB 14102-2005《防火卷帘》‌: 第2.2条要求导轨使用的原材料应符合国家标准,且防烟装置需采用不燃材料‌。导轨若需与防烟装置结合使用,其防火性能需与整体卷帘系统匹配。

重庆消防 2025-03-20 09:33 00 [回复]举报

需要。