自动喷水系统的预作用装置空压机需要强制送检吗?有没有依据


gss123 | 2025-04-30 14:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

EHS专家-DL 2025-04-30 15:05 10 [回复]举报

预作用装置空压机是否需强制送检,取决于其储气罐是否属于压力容器

若空压机配套的储气罐满足以下条件,则属于‌压力容器‌,需纳入特种设备管理并强制送检:

  • 设计压力≥0.1MPa;容积≥30L且压力与容积乘积≥1.0MPa·L。
  • 若空压机储气罐未达到以上压力容器判定标准,则无需强制送检,用户根据《自动喷水灭火系统施工及验收规范》(GB 50261-2017),预作用系统的空压机及气压控制装置应‌定期检查‌,确保其状态正常、压力表显示符合设定值即可。