一个三层的网吧,一层就一个前台,二、三层400平米,除了需要两个疏散楼梯之外,还需要设置什么消防设施,目前无窗户,无排烟,但是设置了独立的烟感报警器,无室内消火栓,无喷淋。

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友68723 2025-05-09 11:39 00 [回复]举报

防软管卷盘或轻便消防水龙,自动灭火系统,并宜采用自动喷水灭火系统,火灾自动报警系统,防烟和排烟设施

李勤 2025-05-09 14:24 00 [回复]举报

报警设施、喷淋设施、排烟设施、消防软管或轻便水龙、应急照明,疏散宽度和距离、出口数量满足要求

牛丫头消防课堂 2025-05-10 00:03 10 [回复]举报

第一,房间总面积超过100㎡,依据《建筑防火通用规范》第8.2.2条,房间总建筑面积大于100㎡的歌舞娱乐放映游艺场所应设置排烟设施;

第二,因为你说现状无窗,所以要设机械排烟;

第三,因为有机械排烟,必须设集中火灾报警系统联动控制机械排烟,你现在独立式烟感不符合要求;

第四,依据《建筑防火通用规范》第8.1.9条,楼层建筑面积大于300㎡的地上歌舞娱乐放映游艺场所,应设置自动喷水灭火系统;

第五,至少是封闭楼梯间,如果不能自然通风,还要考虑加压送风;

第六,应急照明和疏散指示系统;

第七,灭火器;


其他一个个对照吧