消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防灭火救援

大于33m的高层住宅消防电梯可以不设前室吗

加零 | 2022-04-10 12:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

充楞装傻 2022-04-11 09:38 10 [回复]举报

没前室 不叫消防电梯,无法用于救援;

它自己都不能保证安全。烟气、高温都不能抵挡,电梯门耐火极限也不够,而且可能是个好烟囱


大狗狗7 2022-04-11 09:49 10 [回复]举报

消防电梯必须要有前室啊~~~你可以合用,可以共用~~就是不能取消。

十万嬉皮 2022-04-11 10:06 10 [回复]举报

不可以

周家斌 2022-05-07 21:02 10 [回复]举报

GB50016-2014(2018)7.3.5 除设置在仓库连廊、冷库穿堂或谷物筒仓工作塔内的消防电梯外,消防电梯应设置前室,并应符合下列规定:       1 前室宜靠外墙设置,并应在首层直通室外或经过长度不大于 30m 的通道通向室外;       2 前室的使用面积不应小于 6.0m²,前室的短边不应小于 2.4m;与防烟楼梯间合用的前室,其使用面积尚应符合本规范第 5.5.28 条和第 6.4.3 条的规定;      3 除前室的出入口、前室内设置的正压送风口和本规范第 5.5.27 条规定的户门外,前室内不应开设其他门、窗、洞口;      4  前室或合用前室的门应采用乙级防火门,不应设置卷帘。

关闭

关闭

手机APP下载