排烟防火阀关闭风机,控制室主机需要在自动状态么?

ZFX | 2023-07-15 11:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

同同不同 2023-07-15 12:22 20 [回复]举报

不需要,连锁停

鸽芗 2023-07-15 15:55 20 [回复]举报

烟规:4.4.6 排烟风机应满足280℃时连续工作30min的要求,排烟风机应与风机入口处的排烟防火阀连锁,当该阀关闭时,排烟风机应能停止运转。从这个表述看,这是连锁,不经过控制室控制器联动也能行。

阳明心 2023-07-17 17:07 10 [回复]举报

这是连锁,不需要经过控制室控制器联动,跟主机手自动状态无关。

麻溜点   回复: 阳明心2023-09-12 19:20

麻烦问一下。排烟阀启动风机。需不需要主机打自动?

0    0 [回复]举报

潘天坤   回复: 麻溜点2024-06-21 15:09

跟非风机入口处的排烟防火阀是一样的原理,规范没有明确怎么接线。现场如果接控制线,那就不受主机状态影响。现场如果通过报警总线,那么就需要受主机状态影响

0    0 [回复]举报

潘天坤 2024-06-21 15:07 00 [回复]举报

烟规GB51251要求的风机入口处的排烟防火阀是连锁关闭风机,属于接控制线,不受主机状态影响

消防设施通用规范要求的几个位置的排烟防火阀,是否受主机状态影响,不太好说,可能要看现场怎么接线。规范有提到功能要实现,具体怎么实现得看设计和现场实际做法。如果几个位置的全部排烟防火阀均接控制线到排烟风机控制箱,那么就可以不受主机状态影响。如果是总线做法,需要受主机状态影响