救援窗可否兼做排烟窗?

消防救援窗口可否兼做自然排烟窗口使用,前提是双向都满足的前提下。

爱随风 | 2024-05-17 11:34
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

消防检查 2024-05-17 14:04 00 [回复]举报

可以。

逸凡123   回复: 消防检查2024-05-24 10:12

懂规范吗


0    0 [回复]举报

南明离火 2024-05-17 14:40 10 [回复]举报

救援窗距地高度≤1.2米  你排烟窗 不是这个高度区域的吧

一路同行 2024-05-21 10:08 00 [回复]举报

不可以,排烟窗应设在空间高度的1/2以上

潘天坤 2024-06-16 18:01 00 [回复]举报

一般救援窗不可以作为排烟设施。

消防救援窗下沿距室内地面不宜大于1.2米,而排烟设施一般要求在最小清晰高度以上,基本消防救援窗都在最小清晰高度以下。

同时消防救援窗常见为固定窗、门等,非可开启外窗不能作为排烟设施。

如果消防救援窗为可开启外窗,那么还要满足自然排烟相关要求(开启角度、有效面积等)。