各位大神:灭火器配备查了规范只说明了每个点的配备数量,具体没有说明配多少公斤的灭火器?这方面有相关要求吗?请指教,谢谢

红门铠甲 | 2024-06-07 09:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防网友39206 2024-06-09 16:47 00 [回复]举报

应按照《建筑灭火器配置设计规范》GB50140-2005第6.2条灭火器的最低配置基准,来选择具体配多少公斤的灭火器。比如:严重危险级场所,需要满足3A的单具灭火器最小配置灭火级别,按照该规范附录A可知,对于ABC类干粉灭火器,至少要达到5kg方可满足要求,其他以此类推。

潘天坤 2024-06-16 11:04 00 [回复]举报

严重危险级、中危险级、轻危险级场所灭火器的最低配置基准:单具灭火器最小配置灭火器级别分别为3A(89B)、2A(55B)、1A(21B)。

建筑灭火器配置场所的危险等级可以参考规范附录的例子