湿式报警阀压力开关可以躺着安装吗?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 10

张治福 2024-08-30 12:31 00 [回复]举报

不可以,湿式报警阀阀瓣的开启和关闭结构决定了。

磊中   回复: 张治福2024-08-30 17:27

报警阀的阀瓣和压力开关没有关系吧!压力开关构造决定了要竖直安装的,规范规定也是要竖直安装在水力警铃水流通路的管道上,尽量靠近报警阀,以利于启动

0    0 [回复]举报

张治福   回复: 磊中2024-09-02 08:25

湿式报警阀要靠阀瓣的自重压住报警管路的进水孔的,建议去拆开一个湿式报警阀看看内部结构。

0    0 [回复]举报

周家斌   回复: 张治福2024-09-02 11:22

说的是压力开关,不是报警阀组

0    0 [回复]举报

张治福   回复: 周家斌2024-09-02 15:05

我了个擦咧,未审题,此题0分。

0    0 [回复]举报

南明离火 2024-08-30 14:14 00 [回复]举报

规范要求是竖着装

我头发贼黑 2024-08-30 15:24 00 [回复]举报

看图集

周家斌 2024-08-31 16:49 00 [回复]举报

压力开关是水压转化电信号的微动开关,从结构原理来看可以躺着安装的,不同于报警阀组的阀瓣开启原理。

西湾子消防小能手 2024-09-02 14:46 00 [回复]举报

水不干净或有残渣有可能不回位子,线圈进水等问题,存在误报可能

云中飞翔 2025-01-09 10:08 00 [回复]举报

报警阀组压力开关必须竖直安装。