消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

即有车间消防改造(消控室先后有AB两台联动型主机分别担负一个大车间两个区域的火灾自动报警系统)

即有车间消防改造(消控室先后有AB两台联动型主机分别担负一个大车间AB两个区域的火灾自动报警系统)

两个区域合用一套湿式自喷管网,一套消火栓管网系统,一套自喷泵,一套消火栓泵

以上的模式有没有大问题,或者大隐患,技术上容易实现吗

比如湿式报警阀上压力开关,怎么同时连接两台火灾报警控制器联动型

消火栓出水干管上压力开关怎么连接两台火灾报警控制器联动型

两台消防联动控制器怎么各自控制同一组水泵

以上几种电气连接问题通过什么方式或什么元器件解决?在接线端子位置处理吗?

感谢

水清无鱼 | 2024-09-22 22:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

一只小锦Li 2024-09-25 08:36 00 [回复]举报

你这动消防的设备要去报审的吧,要设计院出图,审核后才能施工,施工完后验收,大致是这个流程,不能自己改的

消防网友12661 2024-09-29 16:14 00 [回复]举报

没有任何问题,两个保护对象A车间和B车间,其中水流指示器,信号阀,防排烟,声光广播这些都是各自分开的,只有消火栓泵和喷淋泵共用。

方案一、前提同一厂家的主机

把两个控制器联网做成一个系统,一个主机一个分机,分机和主机负责各自保护对象内的消防设备,把水泵的直启做在主机多线盘上,报警阀压力开关接在任何一个主机均可,因为本身联网了,分机的信息也会发送给主机,同理消火栓出水干管压力开关一旦报警,两台主机都会有报警信息。

报警阀压力开关和消火栓出水干管压力开关启泵的问题:连锁启泵将压力开关和消火栓低压压力开关的线直接接到水泵控制柜就行,都是唯一性的,也不存在什么问题。至于通过火灾报警控制器联动启动的问题,因为联网了,到时后可以通过在主机上通过联动编程来实现,这个给技术员说就可以

水清无鱼   回复: 消防网友126612024-11-10 18:49

你好,请问如果是蓝天和泰和安两部主机呢?泵房消火栓出水干管压力开关作为连锁启动应该没有问题。压力开关输出模块是不是应该分别向两台主机输出信号?是不是需要两个模块?接线怎么扩展?同样情况还有湿式报警阀压力开关的信号输出。以及两台主机如何各自联动启泵?谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载