防火墙或隔墙耐火3H,但是开有风口,有耐火要求吗







1.上图中,防火分区之间隔墙 是防火墙吧,  防火墙或隔墙耐火3H, 图中设置了个 FK-1 风口,70阀的。  这个阀口能保证耐火3小时? 如果不能,岂不是破坏了  防火墙或隔墙耐火3H??


2.为什么在防火墙或隔墙上开这个风口????

知耻也要问 | 2024-11-27 10:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

潘天坤 2024-11-27 13:58 10 [回复]举报

1、如果是作用为防火分隔的墙体一般有一定耐火极限要求,具体是几个小时要看建筑专业定性 

一般的风口无法满足几个小时后耐火极限要求,市场上可能也比较少见能够满足相关耐火极限要求的产品,有见过设置风管+穿墙套管+防火阀+防火封堵(做法不低于墙体耐火极限)+防火包裹这类的设计,个人觉得效果会好一些

2、没看到完整图纸,不确定是什么作用。可以看看安装高度是多少,如果是2米以下,可能是补风口之类的,设备房出来的补风口或者借用相邻分区进行补风而设置的间接补风口

ACEYIN 2024-11-28 17:12 10 [回复]举报

这个应该是防火单元之间用来设置补风的防火百叶开洞吧。以前做项目也有这种作法,苏州当地审图中心也认。之后两本新规后来又有江苏省省标出来,这种做法就不让做了。电动车库必须要用风管机械补风通到防火单元里,不能间接自然补风了