消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

在企业院内,设在辅助用房里面的柴油发电机室和储油间,需要设气体灭火装置吗?

在企业院内,设在辅助用房里面的柴油发电机室和储油间,需要设气体灭火装置吗?

冬天的太阳 | 2023-11-16 16:46
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

阳明心 2023-11-17 09:46 00 [回复]举报

也可以设置推车式ABC干粉灭火器。如果规模较大可设水喷雾,细水雾或气体灭火系统

冬天的太阳   回复: 阳明心2023-12-11 16:04

谢谢

0    0 [回复]举报

我的是昵称 2023-11-17 14:05 10 [回复]举报

不需要。按老的建规,5.4.12  5.4.13 建筑内设有自动喷水灭火系统时,柴油发电机房应设置自动喷水灭火系统。 第8.3.8 条,储油间可采用水喷雾灭火系统、气体灭火系统、泡沫灭火系统或细水雾灭火系统。这一条是可用可不用。换句话说就是,建筑内没有自喷时就不用设了。按危险级别配灭火器。以前的废止了,都不是强条了。

冬天的太阳   回复: 我的是昵称2023-12-11 16:04

谢谢

0    0 [回复]举报

黄辉 2024-01-11 16:40 00 [回复]举报

按《建规》8.3.8条条文说明判断。
(2) 特殊重要设备,主要指设置在重要部位和场所中,发生火灾后将严重影响生产和生活的关键设备。如化工厂中的中央控制室和单台容量300MW机组及以上容量的发电厂的电子设备间、控制室、计算机房及继电器室等。高层民用建筑内火灾危险性大,发生火灾后对生产、生活产生严重影响的配电室等,也属于特殊重要设备室。


是否重要,这个可由业主和设计院判断。

按《建规》5.4.12  5.4.13,也可以设置自喷,不一定要做气体灭火。


关闭

关闭

手机APP下载