消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

集热罩是否还需要设置?

查了50084,未找见对于下喷集热罩/挡水板的相关内容,请问在哪儿能找到对于集热罩/挡水板的相关规范和要求。

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

潘天坤 2024-07-03 22:30 10 [回复]举报

2017年版的自喷设计规范有换了个名词,可以再看看

自动喷水灭火系统设计规范 GB50084-2017第7.1.10条规定:

 挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡,周围弯边的下沿宜与洒水喷头的溅水盘平齐。除下列情况和相关规范另有规定外,其他场所或部位不应采用挡水板:1 设置货架内置洒水喷头的仓库,当货架内置洒水喷头上方有孔洞、缝隙时,可在洒水喷头的上方设置挡水板;2 宽度大于本规范第7.2.3条规定的障碍物,增设的洒水喷头上方有孔洞、 缝隙时,可在洒水喷头的上方设置挡水板

消防网友70367 2024-07-04 09:07 10 [回复]举报

50084第7.1.10条

安洪全 2024-07-04 09:19 20 [回复]举报

没有集热罩的说法

只有挡水板


自动喷水灭火系统设计规范 GB50084-2017

12222刚刚 2024-07-04 10:29 10 [回复]举报

现行规范就没有集热罩这个说法,所以有的消防工程公司说设置了集热罩某些程度上就可以降低喷淋头的设置标准这是错误的

LHH2737 2024-07-04 10:31 10 [回复]举报

阿龙 2024-07-04 10:51 10 [回复]举报

7.1.10 挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡,周围弯边的下沿宜与洒水喷头的溅水盘平齐。除下列情况和相关规范另有规定外,其他场所或部位不应采用挡水板:
      1 设置货架内置洒水喷头的仓库,当货架内置洒水喷头上方有孔洞、缝隙时,可在洒水喷头的上方设置挡水板;
      2 宽度大于本规范第7.2.3条规定的障碍物,增设的洒水喷头上方有孔洞、 缝隙时,可在洒水喷头的上方设置挡水板。

一般只有补偿喷头和上方有空隙的地方才用到。

云霭 2024-07-04 13:33 10 [回复]举报

7.1.10

关闭

关闭

手机APP下载